Garage Heater Electrical Question

I am in need of installing a recently purchased Fahrenheat (FUH 54) forced air garage heater. It is a 17000 BTU, 240volt, 5000 watt, 20.9 amp heater with a max fuse capacity of 30. The installation instructions call for a 10 gauge hard wired.

I have installed a window air condition unit through the wall of my garage which is fed by 240 volt, 10 gauge wire to a single outlet.

My question is, in as much as it is a single outlet and only one appliance at a time can be active, is there any reason I could not use a pigtail from the heater to the same outlet, alternating which one is plugged in on a seasonal basis? I would like to avoid having to run another wire and getting in to the box if at all possible....

I'm assuming the pigtail would need to be 10 gauge to meet mfg. specs.

The heater will be suspended from the ceiling as provided by the mfg. brackets and will be within 3-4 feet of the outlet.

Would a pigtail of this nature be available in local hardware stores (Nashville) or would I need to go to an electrical supply store?

Thanks....

    Advertisement
Reply With Quote Quick reply to this message
Sponsored Links
Advertisement
 
  #2 (permalink)  
Old 12-16-2007, 02:15 PM
F&J F&J is offline
Registered User
 

Last journal entry: 32 Ford cabriolet conversion/windshield
Last photo:
Join Date: Mar 2007
Location: Connecticut
Age: 62
Posts: 1,571
Wiki Edits: 0

Thanks: 0
Thanked 1 Time in 1 Post
If I read it correctly, you have the AC plugged into a 220 wall recepticle. But check the rating on that receptical to make sure it's 30 amp rated. Just the arrangement,angle, & size of the terminal openings should let you know the amps rating.

Then go to either a good hardware store or elect supply and buy the correct plug end and a short length of the 10ga cord wire that is made to be used as a cord. I know Home Depot & Lowes has plug ends in most types, but I never looked for "cord wire by the foot" at those places.

Yes you can buy a pigtail someplace, but it's easy to make one.
Reply With Quote Quick reply to this message
  #3 (permalink)  
Old 12-16-2007, 02:16 PM
Rambo_The_Dog's Avatar
Registered User
 

Last journal entry: Shop Remodel Progress
Join Date: Dec 2005
Location: Pacific Northwest
Posts: 736
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
These electric heaters put more stress on the wiring because the fan cycles for cooling after the heating element has shut down.

My point of view..wire it per the instructions/codes because saving a couple hundred on materials may void your homeowners/shop insurance if something where to ever happen - that something being fire.
Reply With Quote Quick reply to this message
  #4 (permalink)  
Old 12-16-2007, 02:50 PM
Notorious's Avatar
Hot rodder, not street rodder!
 
Last photo:
Join Date: Aug 2007
Location: Bakers Mountain, NC
Posts: 507
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
If the A/C circuit is 10 gauge and 30 amp as is required for the heater, then it wouldn't concern me to get the proper male plug and hook it to a suitable lead from the heater. Then just plug it in as you do the A/C. Probably not code and I'm not an electrician. But I did wire my own house when I built it and the inspector asked me if I did. I told him I did and he said he thought so. Because he said, a contractor usually doesn't do work that neatly! It passed with no problems.
Reply With Quote Quick reply to this message
  #5 (permalink)  
Old 12-16-2007, 02:57 PM
Registered User
 
Join Date: Mar 2005
Location: tacoma wash.
Posts: 74
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
make sure whatever you do it's code! if that heater starts a fire and burns down your house and was improperly insalled the insurance company can tell you "sorry but were not covering that claim!"
Reply With Quote Quick reply to this message
  #6 (permalink)  
Old 12-16-2007, 03:48 PM
302 Z28's Avatar  
Last photo:
Join Date: May 2003
Location: North Texas
Posts: 10,840
Wiki Edits: 0

Thanks: 1
Thanked 86 Times in 73 Posts
The wire will handle the load, just make sure that the breaker feeding the a/c receptacle is 30 amp.

Vince
Reply With Quote Quick reply to this message
  #7 (permalink)  
Old 12-21-2007, 10:08 AM
ztoy's Avatar
speed freak
 
Join Date: Dec 2002
Location: Circleville, Ohio
Age: 60
Posts: 229
Wiki Edits: 0

Thanks: 0
Thanked 1 Time in 1 Post
Quote:
Originally Posted by joeford
I am in need of installing a recently purchased Fahrenheat (FUH 54) forced air garage heater. It is a 17000 BTU, 240volt, 5000 watt, 20.9 amp heater with a max fuse capacity of 30. The installation instructions call for a 10 gauge hard wired.

I have installed a window air condition unit through the wall of my garage which is fed by 240 volt, 10 gauge wire to a single outlet.

My question is, in as much as it is a single outlet and only one appliance at a time can be active, is there any reason I could not use a pigtail from the heater to the same outlet, alternating which one is plugged in on a seasonal basis? I would like to avoid having to run another wire and getting in to the box if at all possible....

I'm assuming the pigtail would need to be 10 gauge to meet mfg. specs.

The heater will be suspended from the ceiling as provided by the mfg. brackets and will be within 3-4 feet of the outlet.

Would a pigtail of this nature be available in local hardware stores (Nashville) or would I need to go to an electrical supply store?

Thanks....

You can use the same recept for either device as long as the recept is rated for 240v and 30a. Then you will need a cord cap with the proper configuration to match the recept. Some 'sjo' cord from an electrical supply house, or maybe from a Home Depot type joint, will work. Just make sure everything is grounded according to code, use #10 or #8 wire and terminate it on a 30a 2 pole breaker.
Reply With Quote Quick reply to this message
  #8 (permalink)  
Old 12-22-2007, 06:03 PM
joeford's Avatar
36 Dream
 

Last journal entry: The fire...
Last photo:
Join Date: May 2005
Location: tennessee
Age: 68
Posts: 201
Wiki Edits: 0

Thanks: 1
Thanked 1 Time in 1 Post
Thanks

Thanks...I checked the box and looks like I have two 20amp breakers tied together....gives me 40amp....Next step is to check the wire gauge, but you gotta think with 40amp it's at least 10ga...thanks again....
Reply With Quote Quick reply to this message
  #9 (permalink)  
Old 12-22-2007, 06:44 PM
123pugsy's Avatar
HOT ROD...... FROM A CHRYSLER?
 
Last wiki edit: Metal shaping
Last journal entry: FLOOR BEADS
Last photo:
Join Date: Apr 2006
Location: Markham,ON
Age: 52
Posts: 2,404
Wiki Edits: 29

Thanks: 473
Thanked 285 Times in 245 Posts
Quote:
Originally Posted by joeford
Thanks...I checked the box and looks like I have two 20amp breakers tied together....gives me 40amp....Next step is to check the wire gauge, but you gotta think with 40amp it's at least 10ga...thanks again....
Huh? Do you have two single 20 amp breakers to get the 240 volts? If so that's still 20 amps.

If you do have a 40 amp breaker, that's too big as max fuse size for your heater is 30 amps.The wire could overheat before the breaker trips.

If you run a cord to plug it in , it should be tied to the cieling using a mesh type hanger.
Reply With Quote Quick reply to this message
  #10 (permalink)  
Old 12-22-2007, 06:55 PM
Kruzin Karl
 
Last photo:
Join Date: Sep 2004
Location: Sunny South Florida
Age: 44
Posts: 153
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
Like Pugsy said, the breaker is there to protect your wire and trip out before it melts or catches fire.

Make sure that you get a double pole 30 amp breaker, It will be one solid breaker with the two "levers" on top tied together.

Everybody is telling you the same thing here, just listen to them and it'll work fine.

Now, the part I'm having a hard time with, is, why do you need a heater?
It was around 80 degrees here today, and I was sweating like a pig working outside today

LOL, have fun staying warm!

Later - Karl
Reply With Quote Quick reply to this message
  #11 (permalink)  
Old 12-22-2007, 11:09 PM
Registered User
 
Join Date: May 2004
Location: MinnESOTA
Posts: 23
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
I don't mean to be negative, but I don't believe that your circuit is adequate.

Generally A/C uses 20amp breakers. That's what I have for my home A/C, which is hard wired. A 40 amp 220 breaker will say 40 amp -- not 20.

My stove circuit has a 40 amp breaker -- and it's labelled 40 amps

Check the wire size in the receptacle -- if your A/C is 20 amp, the wire will probably be 12 gauge.

From your description, the heater will certainly need a 30 amp breaker. -- It could draw 22 - 25 amps. The fan will also draw some -- although nothing too serious.

The pigtails and plugs are also rated for amps. Generally they are rated for
electric dryers and stoves. Dryers are the smaller of the two, I believe.

If you hook up to an underrated circuit with proper breakers, you will blow the breakers on a consistent basis. This will not do your wiring any good.

If your circuit is properly rated, there shouldn't be a problem in plugging in a heater or an A/C. You can only plug one in at a time.

Just trying to help,

ford2go
Reply With Quote Quick reply to this message
  #12 (permalink)  
Old 12-27-2007, 10:20 AM
Registered User
 
Last photo:
Join Date: Feb 2006
Location: ny
Posts: 37
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
Quote:
Originally Posted by joeford
Thanks...I checked the box and looks like I have two 20amp breakers tied together....gives me 40amp....Next step is to check the wire gauge, but you gotta think with 40amp it's at least 10ga...thanks again....
That only gives you 20 amps the way it works is each feed is getting 20 amps of regular old 110/120 V giving you 20 amp 220/240 volts at the motor. I seriously doubt that the electrician would use 10 wire on a 20 amp 220 circuit it would be 12 gauge. I would run a new circuit to the Heater with 10 wire and a 30 amp double pole breaker.
Reply With Quote Quick reply to this message
  #13 (permalink)  
Old 12-27-2007, 11:40 AM
59 wagon man's Avatar
Registered User
 
Last photo:
Join Date: Oct 2006
Location: hollywood fla
Posts: 278
Wiki Edits: 0

Thanks: 0
Thanked 3 Times in 3 Posts
an electric stove i believe uses a 50 amp plug and breaker and the clothes dryer i believe takes a 30 amp plug if it is electric. it is very easy to tell the difference when you look at the plugs side by side .if an electric oven can be wired safely being plugged in then why couldn't the heater
Reply With Quote Quick reply to this message
  #14 (permalink)  
Old 12-27-2007, 07:12 PM
ztoy's Avatar
speed freak
 
Join Date: Dec 2002
Location: Circleville, Ohio
Age: 60
Posts: 229
Wiki Edits: 0

Thanks: 0
Thanked 1 Time in 1 Post
I am a licensed journeyman electrician.

The device is rated at 20.9 amps, not 20. You go to the next size breaker, a 30 amp. It is 240 volt so it requires a 2 pole, 30 amp breaker. The wire size for 30 amps is #10 copper or #6 aluminum. You can legally, according to the NEC, use a larger size wire, but the overcurrent protection must match the rated size per the nameplate. Period, end of story. In addition, since the instructions call for specific wire size, etc, you might want to heed them to protect your warranty, and potentially your or your loved ones life. But its your decision. Listen to advice from a professional or take advice from amateurs, your call.
Reply With Quote Quick reply to this message
  #15 (permalink)  
Old 12-27-2007, 07:34 PM
Marcel
 

Last journal entry: Choo-choo town
Last photo:
Join Date: Feb 2002
Location: adairsville ga.
Age: 72
Posts: 413
Wiki Edits: 0

Thanks: 0
Thanked 1 Time in 1 Post
Garage heater ?

Ztoy, got a ? What does the amperage rating on a double breaker mean. 40 amps ? does that mean that over 20 amps on each leg will throe it, or does it take 40 on either leg to throe it. Thanks
Reply With Quote Quick reply to this message

Recent Garage - Tools posts with photos

Quick Reply
Message:
Options

Register Now

In order to be able to post messages on the Hot Rod Forum : Hotrodders Bulletin Board forums, you must first register.
Please enter your desired user name (usually not your first and last name), your email address and other required details in the form below.
User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.
Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Looking at a garage, flooring question silentpoet Garage - Tools 8 08-02-2006 04:31 AM
hot rod garage question dboyett38666 Garage - Tools 13 05-11-2006 12:40 PM
350 heater hose cooling question 72Nova383 Engine 1 09-16-2004 09:43 AM
painting in garage... water heater concerns? Eddie N Garage - Tools 18 03-09-2003 08:06 AM
Heater control valve question HotRodF100 Engine 2 05-23-2002 03:15 PM


All times are GMT -6. The time now is 02:02 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0 PL2
Copyright Hotrodders.com 1999 - 2012. All Rights Reserved.