Originally Posted by joeford
Thanks...I checked the box and looks like I have two 20amp breakers tied together....gives me 40amp....Next step is to check the wire gauge, but you gotta think with 40amp it's at least 10ga...thanks again....
Huh? Do you have two single 20 amp breakers to get the 240 volts? If so that's still 20 amps.

If you do have a 40 amp breaker, that's too big as max fuse size for your heater is 30 amps.The wire could overheat before the breaker trips.

If you run a cord to plug it in , it should be tied to the cieling using a mesh type hanger.