Lhorn tells us....
Quote;" Since it's a true 220 application (ie the coil on the mag starter is 220 not 110), my understanding is that I dont need a neutral (the middle, L shaped prong on the dryer plug), just 2 hots and neutral. " You don't need a neutral, buy only 2 hots and a neutral? Am I missing somthing here? If you're using a three prong welder plug and receptacle you have two hots and a neutral. How is your welder grounded? I think its not. The trend is (and it may be code, now) to separate the neutral and ground. Dryer plugs and receptacles now have four prongs - two hots, a neutral and a ground. Again, how is your welder grounded? My welder is on a 70 amp 220 breaker. I'd be more concerned about a properly grounded welder than a compressor that puts out air vs. electricity. The best ground for a welder is a conductive rod in the ground that contacts the water table. That's about as rare as a muffler on a Harley. Just pounding a ground rod in doesn't mean you have a perfect ground. Though, better than nothing. |
|
|||||
|
Thanks for the reply. So I'll cut the neutral wire out, and not worry about that. I'm still thinking that I need to ground this thing somehow. Clearly I'm not especially electrically saavy, but I've done a lot of reading and everyone suggests for safety sake to have this thing grounded even though you are correct, it doesn't appear that my welder is grounded either.
You're right about the rod in the ground. I read that the rod is supposed to be like 8 feet long. I'm gonna take a guess that there aren't a ton of people who've gone as far as driving a rod 8 feet into the earth for a ground. |
|
|||||
|
If you are using a three prong welder plug you have two hots AND A GROUND ...not a neutral. If you have a three prong welder receptacle that is wired -two hots and a NEUTRAL it is wired INCORRECTLY!! Your welder does not need a neutral if it is 220, neither does your compressor.
Codes have changed and now require dryer plugs to have four wires...two hots, one neutral, one ground... even if the dryer does not need a neutral. You say you have a "dryer type" plug. If it was originaly wired for a dryer it might have a neutral conductor from the recep to your electrical panel. It might have a ground conductor that is grounded to the box the recep is in. As far as the ground rod goes... you probably have one, as it is required for your service to be grounded and it is usually located underneath your meter enclosure on the outside of your house or building. The ground and neutral are bonded together at the first point of disconnect. From that point on they are seperate as the neutral carries the "return path" for a 120 v. circuit and the ground only sees current in the event of a short. Without going into the theory of electricity you aren't actually consuming the current but merely using it. The 120 circuit path is current out on the hot... current return on the neutral. A 220 circuit relies on the phase "imbalance". This is a kindergarten description, and its really more complicated than that. If you have a welder receptacle, you should wire two hots and a ground. Depending on what you use for wire (conduit and wire... or romex) you should only have three wires... two hots and a ground. If you have romex (or some other bundled cable) that has 4 wires you do not need the 4'th one and it can be cut off and capped on both ends. Check your panel... and if the recep you are using has the third wire on the neutral bar... you should remove it. If it is white in color you should tape it with green and transfer it to the ground bar in your panel. You should also tape the recep end of the wire green to indicate to someone in the future that it is a ground. If the third wire is bare copper make sure it is on the ground bar in your panel NOT the neutral bar. If the third wire is on the neutral bar it will still run... but that is a code violation to have it wired that way. Last edited by JaggedEdge; 11-28-2009 at 06:52 PM. |
|
|||||
|
The 220 recepticle was put in by a licensed electrician. Looks like the wire is orange romex that says "awg 10 grounded type nm-b."
To be honest I'm not sure what type of plug this is. It's only a 3 prong plug. Two flat blade prongs at an angle and a third in middle (triangle formation) that is "L" shaped." Without getting into the panel, is there a way to tell if the L shaped prong is a ground or neutral? Or just in general to tell is a wire is grounded? |
|
||||
|
Jagged Edge is absolutely correct, Yuor welder and compressor must be grounded to your panel only. Do not attempt to ground your equipment by driving a pipe in the ground and not uusing the ground at point of service. The equipment ground must supply a direct path to the overcurrent protection device (circuit breaker) in order to trip that breaker asap. The ground is there for protection of personnel. BTW, I've been electrician for a bunch of years.
|
|
|||||
|
Thank you 35hotrod.. I've been twistin' wire nuts since '87 myself.
If you have orange romex it is fairly recent work as the color code for romex hasn't been around for long. You will have two hots and a bare copper ground conductor in that romex. I will go out on a limb and say if a licensed electrician put it in I would feel confident it is grounded and properly installed. You can pull the recep out without taking the wire off and check if it will make you feel better. Not to imply you're not bright,(its a habit working with new guys) but turn the breaker off first!! My next concern would be the amp draw of the compressor on number 10 wire. Number 10 is good for 30 amps. Check the nameplate of your compressor motor and it should have the amperage on it. Other than that ... you should be good to go with no worries. |
|
||||||
|
The receptacle you are showing is a 30 amp 125/250 volt 3 pole 3 wire. It uses two hots and a ground. It would also be wired with #10 AWG wire. As stated you need to verify the max amps your compressor requires.
Vince |
|
|||||
|
Thanks for the advice guys. I appreciate your patience with my obvious ignorance. I'll do that and pull out the recepticle (after turning off the breaker) to make sure it's grounded. I update my post above with a picture that shows a recepticle similar to mine, so I guess it is an older style dryer type, and not a welder plug.
As far as the 10 gauge, my motor says 22amps on it. I figure it'll pull more on start up so I might be a bit close. If I start tripping the breaker, I'll have to upgrade. It's a pretty short run from my sub box (less than 30 feet) so I'm crossing my fingers that the 10 gauge will be enough. |
|
|||||
|
Glad to help!!!! *****One caution.*****..... if you start tripping breakers.... don't just upsize the breaker
.....The wire size should go up also. I have seen too many situations that resulted in a wire burning because the breaker was too large ( wouldn't trip) and the wire carrying too many amps. A 50 amp breaker can carry wayyyy more amps than a number 10 wire. A 30 amp is the maximum I would put a number 10 wire on.If you have been using this circuit for a welder... chances are you will be ok.. As a side note... breakers should be loaded to no more than 80% their trip value. The value of a breaker is its "trip point" NOT its run capacity. In simpler terms that breaker will trip at a 30 amp load, not carry a 30 amp load. Breaker size for motor loads CAN be calculated at 125% FLA to allow for high current draw or "inrush" at startup. This is ONLY for motor loads. EDIT** If you have it on a 30 and it trips I would recommend upsizing the breaker AND the wire. Last edited by JaggedEdge; 11-28-2009 at 08:15 PM. |
|
|||||
|
You gents are correct. I took a look in the recepticle and in the box and I've got 2 hots (one black, one white) and a big ground wire. So it looks like I'm in business. Thanks for the reminder about upgrading the wire and breaker if needed.
Thanks again guys for sharing your expertise with a noob. It is appreciated tremendously! |
|
|||||
|
With the info you have given I feel sure you should be fine. |
|
|
| Recent Garage - Tools posts with photos |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| larger compressor | gburgess2002 | Garage - Tools | 13 | 07-19-2009 09:36 AM |
| What type of compressor? | Skipr | Body - Exterior | 1 | 05-29-2006 08:00 PM |
| wiper motor won't run | cboy | Electrical | 14 | 05-03-2006 09:44 AM |
| Braided Grounding Strap | 58Chev | Electrical | 9 | 02-13-2006 06:11 PM |
| Overhead Courtsey Light Only Has Dime Glow | JohnTN | Electrical | 3 | 06-07-2005 03:48 PM |