I picked up a 60,000 BTU propane heater at an auction for $10. I don't know much about them. I find hanging clearances and lighting instructions specified on the cabinet, so there's not much left to know.

Just a couple questions, the tag says it must be mounted 8' above the floor. Any particular reason for that? That will be rather difficult in my garage, seeing as how the ceiling is 8' high.

Also, how hot can I expect the vent pipe coming out the back to get? As in, will it be hot enough where I run it through the ceiling and the roof to where I need to buy insulated vent pipe, or will the standard single wall vent pipe suffice? The tag specifies 6" clearance to the ceiling and sides, so I will mount it very close to the ceiling.
Attached Thumbnails
Click image for larger version

Name:	bryant640.jpg
Views:	224
Size:	142.7 KB
ID:	42664  

    Advertisement
Reply With Quote Quick reply to this message
Sponsored Links
Advertisement
 
  #2 (permalink)  
Old 12-19-2009, 12:44 AM
Registered User
 
Last photo:
Join Date: May 2009
Location: Macedon, NY
Posts: 468
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
Hope your garage is bigger than a one car or that thing is going to be overkill. If you'e only got an eight foot high ceiling then you will mount it only as high as you feasibly can maintaining at-least the six inch clearance between the ceiling and the top of the unit. You will need an insulated vent pipe for sure.
Reply With Quote Quick reply to this message
  #3 (permalink)  
Old 12-19-2009, 03:59 AM
1ownerT's Avatar
Home School Valedictorian
 
Last wiki edit: Health and safety in the shop or garage Last photo:
Join Date: Dec 2004
Location: Iowa
Age: 53
Posts: 1,645
Wiki Edits: 4

Thanks: 0
Thanked 3 Times in 3 Posts
You could install a heat shield above it and likely reduce the clearance needed. Definitely use the proper vent pipe.
I would set it up and test fire it before I would put much effort into mounting it to the ceiling.
Reply With Quote Quick reply to this message
  #4 (permalink)  
Old 12-19-2009, 05:53 AM
Registered User
 
Last photo:
Join Date: Dec 2009
Location: IN
Posts: 19
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
The garage is detached, 23' x 23' - a two car unit. Yes, I expect this thing will warm it up pretty fast. It's also not insulated. I know, it needs insulation, but it's just not in the budget right now. The house need more in the attic before the garage needs any. Meanwhile, I'm trying to restore a car in there, and it's winter time.

The thought of firing it up before installing it has crossed my mind. I should do that.

Thanks.
Reply With Quote Quick reply to this message
  #5 (permalink)  
Old 12-19-2009, 08:07 AM
Registered User
 
Join Date: Jan 2007
Location: Plymouth, CT
Posts: 141
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
heat

ask around to some local remodeling contractors- I insulated parts of my
basement with insulation removed during nrenovations which was going to
be thrown out they were happy to save the dumpster space. Jim
Reply With Quote Quick reply to this message
  #6 (permalink)  
Old 12-19-2009, 08:09 AM
wildthing's Avatar
Registered User
 

Last journal entry: time flies
Last photo:
Join Date: Jun 2007
Location: chambersburg, pa.
Posts: 223
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
isn't that the air conditioner that Al bundy bought ? i think it was a kiser .lol
Reply With Quote Quick reply to this message
  #7 (permalink)  
Old 12-19-2009, 09:09 AM
Registered User
 
Last photo:
Join Date: Dec 2009
Location: IN
Posts: 19
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
Ha ha. Yeah, I think Al's Kaiser was a cardboard box with a couple tubes and a crank sticking out of it and painted black. It did put out more hot air than cold air.

I know, this thing is pretty old. That's part of what I like about it. That, and the fact that I got it for $10. I like old cars, old tools and old equipment. Take a look at my mill. It's ancient, but hey, tooling is still available for it and it has a power feed on the X axis. It's massive and heavy and does what I need to do. It was cheap too. No one else wanted it.
Attached Thumbnails
Click image for larger version

Name:	DSCF3063640.jpg
Views:	229
Size:	149.1 KB
ID:	42666  
Reply With Quote Quick reply to this message
  #8 (permalink)  
Old 12-19-2009, 09:32 AM
Registered User
 
Last photo:
Join Date: Dec 2009
Location: IN
Posts: 19
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
Quote:
Originally Posted by jetnow1
ask around to some local remodeling contractors- I insulated parts of my
basement with insulation removed during nrenovations which was going to
be thrown out they were happy to save the dumpster space. Jim
Not a bad idea. I'll check around and see if I can turn anything up.
Reply With Quote Quick reply to this message
  #9 (permalink)  
Old 12-19-2009, 05:48 PM
ogre's Avatar
the 'Duracell Project'
 
Last photo:
Join Date: Nov 2009
Location: Motown
Posts: 1,393
Wiki Edits: 0

Thanks: 0
Thanked 102 Times in 91 Posts
8 ft min is probably an ul listing requirement for grounding or an electrical thingy, lucky for you that doesn't pertain to you, you just need to remember to duck. the only problem i see is you need to vent up to draw the fumes out. if you can vent it throught the roof to get more draw on the flue. if you can't go through the roof, turn the pipe up and a couple feet over the highest point in your roof. either way buy a roof or wall thimble that is used for gas heaters, to keep your garage from burning down. good purchase price, but i think thirdmouse got a better deal on his rube goldburg mill.
Reply With Quote Quick reply to this message
  #10 (permalink)  
Old 12-19-2009, 11:25 PM
327NUT's Avatar
Registered User
 
Last photo:
Join Date: Dec 2004
Location: So. Utah
Age: 67
Posts: 3,250
Wiki Edits: 0

Thanks: 0
Thanked 74 Times in 68 Posts
That thing looks like its about 3' high or so, I would use it like a wood stove in the corner if possible. Build a stand out of block wall cinder blocks mortared together about 1 or 2 corses off of the concrete floor and somehow fasten the heater to it. You only have an 8' ceiling, it would be a lot easier that trying to hang it.
Reply With Quote Quick reply to this message
  #11 (permalink)  
Old 12-20-2009, 12:23 AM
dinger's Avatar
Hotrodders.com Moderator
 
Last wiki edit: Health and safety in the shop or garage
Last journal entry: 36 Ford painting
Last photo:
Join Date: Jan 2002
Location: Visalia, Ca.
Age: 61
Posts: 2,710
Wiki Edits: 1

Thanks: 102
Thanked 110 Times in 76 Posts
I would hang this in a corner, facing out toward the front of the shop, if possible. wonder board with a one inch spacer between the wonder board and the wall or ceiling should give you a good shield to prevent pyrolysis, if this was to be a concern. Sheetrock is dang near fire resistant, but heat with time can be a concern to the structure behind the sheetrock. Test fire it for sure before hanging.

Use the pipe recommend, should be something like hot water heater vent. Go as straight up as possible, use a thimble or flashing through the roof.

There's not a whole lot to these units, a valve, an igniter, a thermocouple, thermopile or 2. Much like a gas dryer, they are easily repaired. Good luck, let us know how this works.
__________________
"When I was younger, I could remember anything, whether it had happened or not." - Mark Twain
Reply With Quote Quick reply to this message
  #12 (permalink)  
Old 12-20-2009, 11:14 AM
59 wagon man's Avatar
Registered User
 
Last photo:
Join Date: Oct 2006
Location: hollywood fla
Posts: 272
Wiki Edits: 0

Thanks: 0
Thanked 3 Times in 3 Posts
had a similar natural gas reznor brand heater in my garage up north you could work in a t-shirt while it was snowing outside. same thing 1 1/2 car garage free standing. hung mine in the corner double wall straight up thru the attic and . use thecorrect roof flashing and vent cap should be no problem . used what we called gimlet rods threaded metal shaft with wood thread on one emd 3/8" thread on other end to mount a piece of unistrut to the roof joists. then the top of the heater usually had a few female threads to insert threaded rod in the top to hang it. you may need more then 1 unistrut setup. you can also use lag boolts to hold the unistrut
Reply With Quote Quick reply to this message
  #13 (permalink)  
Old 12-21-2009, 08:52 AM
MT71c-10's Avatar
too many toys,not enough money
 
Last wiki edit: Garage heating Last photo:
Join Date: Dec 2007
Location: montana
Posts: 102
Wiki Edits: 13

Thanks: 0
Thanked 0 Times in 0 Posts
You must use a B-type venting pipe for your vertical venting. It is a double walled pipe. You will need at least 5' of total vertical venting with 2 1/2 to 3' above the roof. B-type vent pipe requires 1'' of clearance to combustibles.

I would stick to the 6'' of clearance above the unit these units do get hot.

DO NOT mount this on the floor of your shop!!!! Fumes will ignite and you will have a toothpick factory where your shop used to be.

DO NOT run the venting out the side of your shop horizontally. It must go vertical.

MAKE SURE the unit has not been converted back to natural gas and is still propane fired before you hook any gas to it.

DO NOT connect your propane tank directly to the heater.
MAKE SURE you get you get the proper pressure regulator and mount it near the tank. YOU will need about 13 inches of water column of gas pressure going into the gas valve 10 inches at the manifold, any more and it can be dangerous.

Leave about 12'' of space behind the unit to any wall for proper air flow.

Mount the thermostat under the unit on the wall.

The 8' rule would be for fumes and dust combustion. Also because people like to use gas fired units for handy storage, papers on top of them cardboard boxes next to them, VERY BAD IDEAS. Most code only reguire 18'' to the burners on newer appliances, But you have no duct work to route the air flow. Go as high as possible!

You are installing a pressurized gas appliance in an enclosed space, use common sence and be carfull if you are unsure of anything call your local gas company or HVAC shop.

Don't want to get you scared of this just be carefull. Just a small reminder of this.
http://www.youtube.com/watch?v=9irQalM1QH4

Last edited by MT71c-10; 12-21-2009 at 09:11 AM.
Reply With Quote Quick reply to this message
  #14 (permalink)  
Old 12-21-2009, 03:26 PM
Registered User
 
Last photo:
Join Date: Dec 2009
Location: IN
Posts: 19
Wiki Edits: 0

Thanks: 0
Thanked 0 Times in 0 Posts
Floor mounting is not even an option in my garage. Space is at such a premium in here. The garage is 23' x 23' with two cars and two motorcycles in it, and one of the cars is completely disassembled for restoration and all the parts of it are in here. Both motorcycles are easily accessible. When I think about all the large tools and equipment and workbenches and stuff in here, even I am amazed. This garage is an exercise in how much stuff can I get in here and still do anything. I can't walk in a straight line in here anywhere. It's very claustrophobic. You do with what you have.

The gas valve states that it's for propane, as well as the tag on the cabinet. I don't think I can miss there. It came with a regulator on the line. All I have to do at this point is connect it to the tank. The wiring will not remain as it appears here. This is the way I got it. I've used kerosene heaters for many years and I'm conscientious enough to not set combustibles around them. I'd use the one I have out there now, but I can't spare the floor space for it.

The unit stands 28" high. Here is the corner where I will hang it. It won't be 8' off the floor, but there's no way anyone will be walking underneath it. I will have to relocate my sandblast cabinet, probably over in front of the window, and cut some shelving back a little to open up the corner. The camera angle makes it look cramped up there, but there is plenty more than the six inch clearance all the way around that is specified on the cabinet. Being in the corner will allow plenty of room behind it. It will angle out and put most of the hot air right where I usually work. I hope to at least test fire it this week. My brother and his family are visiting next week and he could help me hang it. There is only dial up available where we live and I can't watch anything on utube. I take it that someone's garage is blowing up.
Attached Thumbnails
Click image for larger version

Name:	DSCF3070-640.jpg
Views:	238
Size:	153.0 KB
ID:	42716   Click image for larger version

Name:	DSCF3072-640.jpg
Views:	238
Size:	131.0 KB
ID:	42717  

Last edited by thirdmouse; 12-21-2009 at 03:33 PM.
Reply With Quote Quick reply to this message
  #15 (permalink)  
Old 12-22-2009, 05:53 PM
MT71c-10's Avatar
too many toys,not enough money
 
Last wiki edit: Garage heating Last photo:
Join Date: Dec 2007
Location: montana
Posts: 102
Wiki Edits: 13

Thanks: 0
Thanked 0 Times in 0 Posts
Again I was not and am not trying to get you scared of this unit.!

I'm sure you are more than capable of installing this. When I read your post a couple of red flags went up for me, sounded as if you were "going to plug and play" so to speak. I've been in the heating and air conditioning trade for 12 years, and so I thought I would speak my mind.

These are very simple units, hook up gas, venting, electric and a thermostat, light the pilot light and your cooking.

I don't think hanging it lower than 8' feet would be bad, it happens all the time, But just something the manufacture must put in writing.

I would guess that your good with the propane gas feed, But I have seen mobile homes that are marked for propane running natural gas. This is hard to tell usually the propane orifices are smaller and run at slightly higher gas pressure. So if you hook up your propane tank and get it running, it should light fairly smooth (if the unit has not been serviced in a while it may light rough) BUT if there is any flame spilling out of the burner tubes, or the flame is very blue SHUT IT DOWN, and have a hvac guy look it over. Check your pressure regulator it should have either have a pressure of IN. WC. or PSI cast into it or on a rating plate. If it does not have one marked or is over 14 in. wc. (or 0.48 psi) do not use it.

The youtube was just one video of a big natural gas explosion we had not quite a year ago. It took out 3 100 year old buildings in the middle of our downtown, just a little reminder that it really can go BOOM.

So i'm sure you can do this safely, your on the right track. Any questions just give me a buzz. Good luck and enjoy your heat!

So after I read the post I looked into the wiki, and found a good start to garage heating, but lots to be written. So I did add some, I will continue to add as time allows.
Reply With Quote Quick reply to this message

Recent Garage - Tools posts with photos

Quick Reply
Message:
Options

Register Now

In order to be able to post messages on the Hot Rod Forum : Hotrodders Bulletin Board forums, you must first register.
Please enter your desired user name (usually not your first and last name), your email address and other required details in the form below.
User Name:
If you do not want to register, fill this field only and the name will be used as user name for your post.
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.
Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
OXY~ACETYLENE !!!!! Safety!!!!!!!!!! Rob Keller Garage - Tools 59 01-08-2010 06:48 PM
Installing Heater Core Cases 64 Impala SS 64Joker Hotrodding Basics 0 03-09-2007 03:42 PM
Forced Air Propane Space Heater JimKramer Garage - Tools 3 12-08-2005 01:50 PM
hanging heater installation 61wagonair Garage - Tools 18 06-23-2005 06:36 PM
351M on Propane... Fuel Mileage!!! offroadin Engine 20 09-26-2004 10:12 AM


All times are GMT -6. The time now is 12:22 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0 PL2
Copyright Hotrodders.com 1999 - 2012. All Rights Reserved.