Hot Rod Forum : Hotrodders Bulletin Board - Reply to Topic
Hotrodders.com -- Hot Rod Forum



Register FAQ Search Today's Posts Unanswered Posts Auto Escrow Insurance Auto Loans
Hot Rod Forum : Hotrodders Bulletin Board > Tech Help> Garage - Tools> Wiring subpanel
User Name
Password
lost password?   |   register now

Thread: Wiring subpanel Reply to Thread
Title:
  
Message:
Trackback:
Send Trackbacks to (Separate multiple URLs with spaces) :

Register Now

In order to be able to post messages on the Hot Rod Forum : Hotrodders Bulletin Board forums, you must first register.
Please enter your desired user name (usually not your first and last name), your email address and other required details in the form below.
User Name:
If you do not want to register, fill this field only and the name will be used as user name for your post.
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.
Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.



Additional Options
Miscellaneous Options

Topic Review (Newest First)
11-16-2011 07:19 PM
timothale
starting load.

In my old shop I had a100 amp sub panel. 145 ft from house main panel to shop. The distance from the main panel to the sub panel determines the wire size needed. I used the minimum size per code calculation and the lights used to go dim when someone was welding and the 5 Hp air compressor kicked in. In the new 40 x 120 ft shop my son who is an electrical contractor put in a new feed from the power pole and a 200 amp main panel, 42 circuit and added a 60 amp sub panel next to the lift. seperate feeds to all of the bigger machinery, welder. lathe, mill. chop saw,etc , only 6 general use outlets per circuit breaker. . The wood side got feeds for planer, table saw, turret saw, sawdust colledtor. etc and the lights don't dim.
11-16-2011 02:58 PM
Bmacdona It's going to depend on the size of your compressor motor. a 3hp single-phase motor @240v will draw somewhere around 18A or so. You'll need to check the data plate on the motor itself for HP/amperage draw. The 140 will pull about 15A@115V and you'll also want to take into consideration anything else that you'll be running off the panel....lights, fans, heaters/AC, etc. If after adding up all the numbers, you're comfortable with the 60A breaker (that it also gives you room for expansion), then it shouldn't be a problem. You'll probably want to consider oversizing the feed wire, depending on the actual distance between the boxes.
11-16-2011 01:36 PM
thatshimman
Wiring subpanel

I have a millermatic 140 and a Morgan air compressor that requires 240v. Would it be safe to say that a 100 amp subpanel with a 60amp breaker from the main allow me to utilize both devices simutaneously? That sounds like overkill to me.

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT -6. The time now is 04:16 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0 PL2
Copyright Hotrodders.com 1999 - 2012. All Rights Reserved.