Hot Rod Forum : Hotrodders Bulletin Board - Reply to Topic
Hotrodders.com -- Hot Rod Forum



Register FAQ Search Today's Posts Unanswered Posts Auto Escrow Insurance Auto Loans
Hot Rod Forum : Hotrodders Bulletin Board > Tech Help> Electrical> 240 volt extension cords
User Name
Password
lost password?   |   register now

Thread: 240 volt extension cords Reply to Thread
Title:
  
Message:
Trackback:
Send Trackbacks to (Separate multiple URLs with spaces) :

Register Now

In order to be able to post messages on the Hot Rod Forum : Hotrodders Bulletin Board forums, you must first register.
Please enter your desired user name (usually not your first and last name), your email address and other required details in the form below.
User Name:
If you do not want to register, fill this field only and the name will be used as user name for your post.
Password
Please enter a password for your user account. Note that passwords are case-sensitive.
Password:
Confirm Password:
Email Address
Please enter a valid email address for yourself.
Email Address:

Log-in

Human Verification

In order to verify that you are a human and not a spam bot, please enter the answer into the following box below based on the instructions contained in the graphic.



Additional Options
Miscellaneous Options

Topic Review (Newest First)
07-14-2006 05:24 PM
cucumber1949 10AWG conductors should be fine for 240 volt, 40 amps, single phase, copper, at a length of 30 feet. Actually 12AWG is the minimum wire size with a 3% voltage drop. Ampacity limits this to 30 amps though for RUW, T or TW insulation on the cord. If the insulation on the cable was FEP, FEPB, THHN, or XHHW then 40 amps max would work for 12AWG - the limiting factor is the insulation material, not the conductor material (the insulation would begin melting before the copper conductor).

The 10AWG conductors will only drop the voltage 1%, which is not a problem as most line voltages fluctuate way more than that on a regular basis.

If you are still interested in an extension cord, I made one for a 240V mill/drill machine - went to Lowes and bought a leftover length of AWG 10.3 and the proper plugs for each end of the cord. Total cost $28. Properly assembled, this should serve you well.

If you are going to run it outside between two buildings, the underground conduit is good advice. If you place this in a conduit, then 10AWG would be the minimum as the above is for free-air (no conduit) installations. Also, most plastic-sheathed cables should not be exposed to sunlight unless explicitly stated otherwise.
07-14-2006 04:58 PM
CDJr Right-O, doc I prefer running larger than needed wiring too, instead of "just enough"...hell, my compressor is only rated at 10-12 RLA and I still ran #10 to it with a 30A breaker. Like you said, better safe than sorry. I would use #8 but with a 40A breaker cuz that 5 hp motor may draw 30 or better on startup, and a 30A breaker will weaken over time with a full load through it and eventually start tripping when the compressor starts up.
07-14-2006 04:43 PM
docvette Doc here,

No the reason I specified 8, is the wire is larger than required for the draw because of possible rotor locks, and changing conditions of the compressor, as was mentioned, Compressors are not stable load items..(less heat, more power to the load) and the 30 amp breaker to limit the amount of draw between the line and the load closer to the spike load.

Better safe than sorry..and I am assuming it's under 100 foot run ..

Doc
07-14-2006 04:35 PM
CDJr Ummm, doc, I think youre thinkin of #10 thatll carry 30 amps. For a 5 hp motor, you need to run #8 wire and use a 40 amp breaker, jon.
07-14-2006 04:18 PM
docvette Doc Here,

746 Watts is 1 HP...or in your case 4100 watts..

P/E= about 18 amps..

BUT this is in a perfect world..That would assume the compressor was steady and not cycling (High / low Rotor load) and Does not account for startup rotor load...nor does it assume, line loss or switch gear loss..

30 Amp 8 awg for a short distance would be fine..

As was said before if the house and garage isn't too far, and you have a slot for the breaker, you can get some 1 inch conduit, Ell's, 90' Condulets, whatever is needed..rent a bender, and install a permanent location yourself without too much trouble.

Doc
07-14-2006 07:42 AM
oldred "Compressor HP ratings can be a bit erroneous"

That's letting them off easy!, Comical would be a more apt description.
07-14-2006 05:50 AM
302 Z28 Compressor HP ratings can be a bit erroneous. You must provide us with the motor nameplate amperage draw before we can tell you what size wire you need. More than likely the 3/conductor #10 will be adequate for the distance you mentioned though.

Vince
07-14-2006 04:47 AM
CDJr What size breaker is feeding the existing outlet? And how far from the box is the outlet and shed? If youre mechanically inclined and safety-conscious, you could probably run a new line yourself.
07-13-2006 03:58 PM
jonfoster71
240 volt extension cord

i was thinking a 10.3 wire 30amp compressor should be 20 amp about 30' or less
07-13-2006 03:13 PM
docvette Doc here,

Sure, provided: The ampacity of the Cord IS NOT exceeded by the current draw of the compressor for the length of the run in footage, AND the Plugs Mate and LOCK when connected, AND the compressor is properly grounded, And meets local code requirements.

You can probably Find a proper cord at A Contractor's Supply outlet.

Doc
07-13-2006 02:31 PM
jonfoster71
240 volt extension cords

i'm getting ready to buy a 80gal 5.5 hp compresser for my 65 mustang job the contractor wants a boat load to instale the 240 line i need in my shed can i get away with running a heavy extension cord to it i have a 240 outlit on the sid of the house for a welder

Posting Rules
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


All times are GMT -6. The time now is 01:14 PM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0 PL2
Copyright Hotrodders.com 1999 - 2012. All Rights Reserved.