Quote:
Originally Posted by roger1
To my understanding, he has a 30 Amp receptacle that is dedicated running #10 wire with a 2 pole 30 Amp breaker.

He will either plug a 30 Amp dryer into this receptacle or unplug the dryer and plug in a welder (with an extension cord) which is supposed to be on a 20 Amp 220V circuit.

So, the problem isn't what you state. And, the problem isn't running the dryer, it is running the welder on a 30 Amp breaker when it is designed for a 20 Amp circuit.
If his extension cord is #10 then he's probably running Romex as an extension cord which is not designed for that.
If he is using a standard extension cord, the largest available for those is #12 and it wouldn't be good to run #12 wire on a 30 Amp breaker.
roger1............this "extension" I described is not your typical wire lying on the ground. It is #10 armored cable wired the same way you would run any line in a house. The only difference it that the input end is not wired into the main panel. It terminates in a junction box near the dryer to which I have a standard dryer cord spliced into. I'll post some pics later.