Another question: I am running a line from the current dryer 240V outlet out to the garage. The dryer outlet is on a separate line and has a subpanel with two 20V breakers just above the outlet. The line to the garage is going to be basically an extension and not hardwired into the circuit. I will unplug the dryer and plug in the extension line. The dryer circuit is on 12 gage wire (or at least it should be). Since the extension line to the garage is about 55 feet, should I run 10 gage or stick with 12 gage? Also, there should be no difference in wiring for a dryer other than it may have a neutral wire included........correct? |
|
||||||
|
Quote:
Vince |
|
||||||
|
For a 15 amp compressor use a 2 pole 20 amp breaker and 12-2 w/ground Romex. If it was a long distance run, then go to 10-2.
Anything more is overkill and using a 30 amp breaker is the wrong thing to do. Last edited by roger1; 12-09-2008 at 08:21 PM. |
|
|||||
|
The circuit breaker size is only loosely associated with the load. The wire size for a motor load starting a compressor could be heavier than a #10 for a 30 amp circuit. #10 might be fine for a dryer but you might need #8 or possibly #6 depending on the distance and the load, ie if the compressor starts hard.
A good rule of thumb is to take 125% of the running amps then look at what circuit breakers would be suitable, at 80%. So, a 20 amp compressor would be 25 amps for calculation sake and a 30 amp breaker would be 24 amps so a 40 amp breaker with a minimum of #8 would be used. |
|
||||||
|
Quote:
Old code would be 10-2 w/ground and new code is 10-3 w/ground. |
|
|||||
|
Quote:
|
|
||||||
|
Quote:
No it does not. In the case of a dryer using 10-2 wire, a neutral is not used. Where 10-2 wire was used (old code) the receptacle and plug should be 3 prongs. In new installations (10-3 wire) a 4 prong receptacle and plug are used. You shouldn't install a 4 prong receptacle when 10-2 wire is used. (It would work, but it's the wrong thing to do.) If you have a 3 prong receptacle and a 4 prong plug on a new dryer, your dryer cord should be changed to a matching 3 prong plug. Your big box hardware stores will carry the cords. |
|
|||||
|
Quote:
|
|
|||||
|
In a residential install, the neutral will be ground. You need to tape it green and re-land it to the ground bus if there is one. With this outlet, you need to run a minimum of #8, so the dryer circuit wiring will be too light if that's what you used.
|
|
|||||
|
Quote:
|
|
|||||
|
more electrical
My son is and electrical contractor- and master electrician. Now I ask him what are the new rules in the 'NEC. As stated in previous posts wire size depends on the wire distance from the breaker to the load and overload calculation... An electric dryer has 110 volt control-timer and the rotation motor is 110 volts which doesn't have and much starting power requiremenrts
|
|
|||||
|
The maximum wire size is governed by one of three things. 1) If the load is a motor load like a compressor which has a high current start out of proportion to the running current, 2) the distance between the circuit breaker and the load causes voltage drop, or 3) if you have a certain plug configuration as is your case. A 10 gauge wire will not support a 50 amp circuit.
You need to install the correct sized wire and circuit breaker. |
|
||||||
|
Quote:
That may be the wrong one for your dryer. I have never seen an electric residential dryer that wasn't 30 Amps. 50 Amp will require #8 and 30 Amp requires #10. |
|
|
| Recent Garage - Tools posts with photos |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Used compressor - rusty tank? | Slipangle | Garage - Tools | 15 | 03-16-2012 08:51 AM |
| wiring in air compressor | mitmaks | Garage - Tools | 60 | 04-14-2007 05:02 PM |
| air lines | CARGUY | Garage - Tools | 96 | 11-16-2006 04:11 PM |
| Wiring an Hour Meter to my Compressor. | 58Chev | Garage - Tools | 6 | 12-18-2005 10:24 AM |
| Wiring my 230v compressor...... | PairOf69's | Garage - Tools | 7 | 11-18-2005 08:04 PM |